GFCI Problems #6475750 08/03/11 10:36 PM
Joined: Jun 2005
Posts: 12,923
DanDaBald Offline OP
TFF Guru
OP Offline
TFF Guru
Joined: Jun 2005
Posts: 12,923
I provide network support for apartment complexes. The network equipment is outdoors in metal boxes hung on the walls of the buildings. The network equipment is plugged into (not hard-wired) outlets on the outside of the buildings that have the hinged plastic covers on them. The duplex outlets on the outside of the buildings are all connected to one GFCI per building. So if the GFCI trips the network goes down and I get a service call. Good for me 'cause I get paid by the call.

We have an installation in Grand Prairie that trips 3-5 GFCI's per week - on different buildings at different times of the day - no rhyme, no reason, no particular pattern that we can tell. Yesterday I had to reset the GFCI on building 3, tomorrow I have to go reset the GFCI's on buildings 2 & 9.

Is it the heat? Maybe, but the installations of the same basic system is running fine in Frisco, Fort Worth, Las Vegas and other locations.

The folks I work for would entertain the (paid) assistance of a licensed electrician to investigate this problem - so that we can present the findings to the Apartment Complex and they could fix the problem. I'm sure it will be difficult to trace to the root cause as it takes just a very small amount of leakage current to trip AND it's a very intermittent problem.

a - any licensed electricians here that would know how to fix this problem?
b - could you PM me contact information
c - no, I have NOT tried the obvious answer nor will I . . . .


flag NEVER FORGET 9/11/2001 flag
Re: GFCI Problems [Re: DanDaBald] #6476434 08/04/11 01:59 AM
Joined: Jul 2011
Posts: 511
L
lavonfisher Offline
Pro Angler
Offline
Pro Angler
L
Joined: Jul 2011
Posts: 511
I would not imagine that heat has anything to do with power since this is Texas after all. It would have to be something to do with the apartment complexes. A/C units are probably running full load and people probably have an overload of power going through.

Last edited by lavonfisher; 08/04/11 02:03 AM.
Re: GFCI Problems [Re: lavonfisher] #6476797 08/04/11 03:47 AM
Joined: Feb 2010
Posts: 2,929
A
angler management Offline
Extreme Angler
Offline
Extreme Angler
A
Joined: Feb 2010
Posts: 2,929
i am a lisenced journeyman electrician. gfci's trip ONLY when there is a difference in voltage coming from the source and the voltage returning on the grounded conductor (neutral). most of the time, the problem is with what you have plugged into a gfci protected circuit. one other thing. electricity could care less what the temp. is until you get into the thousands of volts and the heat doesn't have a way to escape.

Last edited by angler management; 08/04/11 03:49 AM.
Re: GFCI Problems [Re: angler management] #6478468 08/04/11 05:46 PM
Joined: Nov 2010
Posts: 6,124
C
CrappieHappy Offline
TFF Celebrity
Offline
TFF Celebrity
C
Joined: Nov 2010
Posts: 6,124
you should check into a dedicated power circuit vs. plugging into a GFCI circuit....


Take a Kid Fishing.....

[Linked Image]


TNT Tackle

JigCraft.com
Re: GFCI Problems [Re: CrappieHappy] #6479315 08/04/11 08:51 PM
Joined: Jul 2011
Posts: 511
L
lavonfisher Offline
Pro Angler
Offline
Pro Angler
L
Joined: Jul 2011
Posts: 511
Agreed. Hospitals install dedicated circuits for such systems as data, a/c so that in case power goes out, patient support etc. does not go out as well.

Re: GFCI Problems [Re: lavonfisher] #6479933 08/04/11 11:04 PM
Joined: Jun 2005
Posts: 12,923
DanDaBald Offline OP
TFF Guru
OP Offline
TFF Guru
Joined: Jun 2005
Posts: 12,923
Thanks for all the good replies - but we're adding a grand total of less than 100 watts' usage to an existing circuit that doesn't have much draw to begin with as the outlets are convenience outlets for AC techs and sprinkler controllers - and most of those are unplugged.

I'm starting to think the GFCI outlets belong indoors and the GFCI BREAKERS are for outdoor applications . . . . (?)


flag NEVER FORGET 9/11/2001 flag
Re: GFCI Problems [Re: DanDaBald] #6480786 08/05/11 02:37 AM
Joined: Feb 2010
Posts: 2,929
A
angler management Offline
Extreme Angler
Offline
Extreme Angler
A
Joined: Feb 2010
Posts: 2,929
how much of a draw whatever equipment you have plugged into doesn't matter. gfci's belong outside because the national electric code says so. there are exceptions, however. i'm not a good explainer. this might help:

http://ecmweb.com/mag/electric_think_gfci/

Re: GFCI Problems [Re: angler management] #6480906 08/05/11 03:07 AM
Joined: Jun 2005
Posts: 12,923
DanDaBald Offline OP
TFF Guru
OP Offline
TFF Guru
Joined: Jun 2005
Posts: 12,923
Thanks for the link and I do agree with the reasoning - however - at this particular complex there is ONE GFCI in series with SEVEN other duplex outlets - the problem could lie in any area within maybe 150' of wire and connections. From your link:
Length of circuit. A GFCI is subjected to tests that simulate long branch circuits. While there are no specific rules concerning the length of the circuit protected or the number of receptacles on the protected circuit, remember that the GFCI will add up all the harmless leakage currents and capacitive leakages. Under extreme circumstances, this could "preload" the GFCI and make it appear overly sensitive or, worst case, result in nuisance tripping. Therefore, you should minimize the length of circuits to the degree possible.

I heard from hopalong123 that at 60' things start go get flaky - these buildings are way over the limit imho.

I can't get them to rewire the building for the equipment I try to keep running.

They had a water break in building 9 on Tuesday afternoon - since, the GFCI for the outside outlets has failed to reset - somewhere it's wet and current is leaking - I can't fix it......

Thanks for all the good info - the TFF OT at its best.


flag NEVER FORGET 9/11/2001 flag
Re: GFCI Problems [Re: DanDaBald] #6481132 08/05/11 04:23 AM
Joined: Mar 2008
Posts: 311
J
Johnny_J_JaMata Offline
Angler
Offline
Angler
J
Joined: Mar 2008
Posts: 311
Heat won't have anything to do with it but the humidity can.

Couple things i'd look at would be is the gfi in the middle or beginning of the recpt circuit? Could be that if someone is plugging in any kind of device with a motor (vacumn, any kinda pump, etc) could cause it to trip. Gfi's don't like motors. But if the gfi is at the end of the series, that's prob not it.

If it's a cheap brand of gfi, it could also be the problem.

I would look into getting a recept dedicated for the network hub that is not accesible to the general public. Put it inside the metal box if possible and lock the box. Or make a hardwire connection to the hub, it can be done.

Re: GFCI Problems [Re: Johnny_J_JaMata] #6490692 08/08/11 03:07 AM
Joined: Oct 2006
Posts: 17,725
S
StephenB Offline
Bucket Expert
Offline
Bucket Expert
S
Joined: Oct 2006
Posts: 17,725
Probably the same brownout stuff that is messing up capacitors on everybody's A/C systems these days.


Re: GFCI Problems [Re: StephenB] #6490794 08/08/11 03:48 AM
Joined: Jun 2005
Posts: 12,923
DanDaBald Offline OP
TFF Guru
OP Offline
TFF Guru
Joined: Jun 2005
Posts: 12,923
I think the main problem at this complex is the length of the runs - each GFCI is in series with at least 6 other duplex outlets. For the most part, the other outlets have no load - they are convenience outlets for AC Service.

Long runs, lotsa heat, occasional AC Service Person = tripped GFCIs

I get paid every time I go out there to service them . . . . Good thing.


flag NEVER FORGET 9/11/2001 flag
Re: GFCI Problems [Re: DanDaBald] #6491314 08/08/11 01:15 PM
Joined: Dec 2008
Posts: 16,027
G
grout-scout Online Sleepy
TFF Guru
Online Sleepy
TFF Guru
G
Joined: Dec 2008
Posts: 16,027
Not an electrician here but I have seen the gfci's get weak over time and just reset on themselves. If they are over 5 years old I'd just replace them with the heavier duty gfci. $15 bucks for a new plug would be alot cheaper than having to pay you.

Re: GFCI Problems [Re: DanDaBald] #6491332 08/08/11 01:24 PM
Joined: Jun 2008
Posts: 943
S
Stickchunker Online Content
Pro Angler
Online Content
Pro Angler
S
Joined: Jun 2008
Posts: 943
This.

"I would look into getting a recept dedicated for the network hub that is not accesible to the general public. Put it inside the metal box if possible and lock the box. Or make a hardwire connection to the hub, it can be done"

A dedicated circut will solve all of your problems.